DRAFTCONCEPT ORDINANCE No. 132 NO. SS
AN ORDINANCE OF THE BOARD OF DIRECTORS OF THE
MONTEREY PENINSULA WATER MANAGEMENT DISTRICT
ADDING RULE 23.6 TO ESTABLISH A WATER ENTITLEMENT FOR
THE PROCESS FOR ISSUING WATER USE PERMITS
FINDINGS
1. The
2. MPWMD
has general and specific power to cause and implement water conservation
activities and to cause sufficient water to be available for present and future
beneficial use or uses of lands or inhabitants within the District as set forth
in Sections 325 and 328 of the Monterey Peninsula Water Management District
Law.
3. The
4. In
2006, [1]
5.
6. The
Project includes the construction of a municipally owned desalination facility
in [2] The Sand City Desalination Facility shall
extract brackish water from the Aromas Sands aquifer and remove salts from that
brackish water. Potable water produced
by the Sand City Desalination Facility shall be delivered through a single
connection into the existing California American Water distribution system (“CAW System”) pursuant to MPWMD WDS Permit
No.’s M07-02-L4 and M07-03-L4 (collectively, the “WDS Permits”).
7. Operation
of the Sand City Desalination Facility shall be regulated by the California
Department of Health Services.
8. This
ordinance shall allow water produced by the Sand City Desalination Facility to
be delivered through a single connection into the CAW System.
9. This
ordinance shall allow the expansion and extension of the CAW System to provide
connections to, and potable water service in specific annual quantities
(expressed in acre-feet) for the use on and benefit of all property located
within the jurisdictional limits of Sand City (the “Sand City Sites”).
10. In
consideration for the delivery of water from the Sand City Desalination
Facility to the CAW System, this ordinance shall establish a Water Entitlement
in favor of [3]
11. The
Water Entitlement established by this ordinance shall be separate and distinct
from the Allocation to [4]
12. This
ordinance authorizes [5]
13. This
ordinance shall allow issuance of the Sand City Water Use Permits authorized by
this ordinance for new and expanded water uses on the Sand City Sites, in a
cumulative amount of no more than 206 acre feet per year.
14. This
ordinance provides that water use authorized by Water Permits issued under this
ordinance shall be subject to the conservation Rules of MPWMD under its
Regulation XIV and the rationing Rules of MPWMD under MPWMD its Regulation XV except as
otherwise provided herein.
15. This
ordinance shall add Rule 23.6 and amend Rules 11, 21 and 23.1 to the Rules and
Regulations of the Monterey Peninsula Water Management District.
16.
17. The
18. It
is in the public interest to reduce the amount of water diverted from the ,
if successful, will have the environmentally beneficial effect of
reducing CAW’s current reliance on its existing sources of water supply.[6] The Project will provide an immediate benefit
to the environment by allowing a 300 acre-foot per Water Year reduction of
demand on existing sources of water supply for the CAW System at the time the
Project becomes operational. The Sand
City Water Entitlement allows a maximum of 206 acre-feet of new or expanded uses
to be added to the CAW System for use on the Sand City Sites. The remaining , and a
permanent reduction of 94 acre-feet of water will be permanently added to
CAW’s System by the Sand City Desalination Facility and
thereby result in a permanent 94 acre-foot reduction in annual
pumping demand from the Carmel River and/or the Seaside Groundwater Basin.which is equal
to the amount of water supplied to the Sand City Sites by the CAW System during
the most recent completed Water Year.[7]
19. California
American Water has been limited in its ability to deliver potable water by
California State Water Resources Control Board (“SWRCB”) Order No. WR 95-10, dated
20. The SWRCB has concluded that the Project, including the delivery
of water represented by the Water Entitlement to the Sand City Sites, does not
violate any provision of Order No. WR 95-10.[8]
21. The
Project will allow for the expansion of commercial and residential water uses
within
22. It
is in the best interest of MPWMD and the inhabitants thereof to provide for the
Water Entitlement and to enable the Sand City Water Use Permits.
23. The
Project is consistent with the goals and strategic objectives of MPWMD.
NOW THEREFORE be it ordained as
follows:
Section One: Short Title
This ordinance shall be known as the
Sand City Water Supply Project Entitlement Ordinance of the Monterey Peninsula
Water Management District.
Section Two: Purpose
A. The
primary purpose of this ordinance is to facilitate the Project. Contemporaneously with the adoption of this ordinance,
the Board of Directors of MPWMD may
approve an application by Sand City for a Water Distribution System Permit
allowing the 300 acre-feet of water to be produced annually by the Sand City
Desalination Facility to be put into the existing CAW System. The addition of the Sand City
Desalination Facility as a Source of Supply to the CAW System shall temporarily
decrease demand on existing water sources for the CAW System. [9]
B. The WDS
Permits allow CAW to take delivery into the CAW System of the 300 acre-feet per
Water Year of Potable Water to be produced by the Desalination Facility. This ordinance establishes a
Water Entitlement for 206 acre-feet per Water Year of Potable water (the “Sand City Water Entitlement”) which allows
up to 206 acre-feet of Potable Water to be distributed from the CAW System for
new or expanded water uses on the Sand City Sites as evidenced by
a Water Use Permit. The Water Use Permit authorized
by this ordinance shall allow for new and expanded water uses within Sand City.
Contemporaneously with the adoption of
this ordinance, the Board of Directors of MPWMD may approve an application by
California American Water to expand the CAW System to allow for the delivery of
up to the entire amount of the Sand City Water Entitlement to new and expanded
water uses on the Sand City Sites.
C. This
ordinance authorizes [10]
Section Three: Rule 23.6
Rule
23.6 is hereby added to the Rules and Regulations of the Monterey Peninsula
Water Management District to read as follows:
RULE 23.6 -
A. There
is hereby established the Sand City Water Entitlement which confers upon Sand
City a vested property right to take up to 206 acre-feet per Water Year of Potable
water from the CAW System. California
American Water shall be required to take delivery of 300 acre-feet per Water
Year of Potable water from the Sand City Desalination Facility for so long as
the Sand City Water Entitlement continues.
The Sand City Water Entitlement shall continue until December 31, 2082.[11]
B. [12] Any portion of the Sand City Water
Entitlement conveyed to the owner of a Sand City Site shall become vested in
the owner of the Sand City Site, and appurtenant to title to the particular
Sand City Site, at the time a Sand City Water Use Permit is issued as evidence
of such conveyance. At the time the Sand City Desalination
Facility begins delivery of Potable water to the CAW System, the General
Manager shall issue a Water Use Permit to
C. The
Sand City Water Entitlement shall be separate and distinct from the Allocation
to [13]
D. Nothing
in this ordinance shall excuse the owner of a Sand City Site from the
obligation to comply with the water conservation rules set forth in MPWMD
Regulation XIV and the water rationing rules set forth in MPWMD Regulation XV, provided,
however, that MPWMD shall not impose a moratorium on the issuance of Water Use
Permits authorized by this ordinance.
E. Nothing in this ordinance shall relieve the
owner of a Sand City Site to whom a Sand City Water Use Permit has been
issued from any all or any part of such owner’s obligation to pay all fees,
connection charges, user fees, surcharges, taxes, utility taxes or other
obligation imposed by the California Public Utilities Commission, the MPWMD
(including but not limited to fees and charges imposed by MPWMD under its Rule
24), California American Water or any governmental authority acting with
jurisdiction on other users of the CAW System in Sand City. Nothing herein shall prevent the termination
of service from the CAW System for non-payment of required fees and charges in
the manner authorized by law.
F. Each Water
Use Permit issued to the owner of a Sand City Site shall provide that MPWMD
shall have such access as may be required to enable it to account for the use
of water on the Sand City Site. Water
use authorized by the Water Use Permit shall be measured in accordance with the
water use factors specified at the time of issuance of the Water Use Permit.
Section
Four: AMENDMENT TO RULE 21-E: APPLICATION FOR WATER USE PERMIT FOR
“BENEFITED PROPERTIES” AS THAT TERM IS DEFINED IN RULE 11, 23.5 and 23.6
Rule 21-E[14]
shall be revised as shown in bold italics (bold italics) and
strikeout (strikeout):
E. APPLICATION
FOR WATER USE PERMIT FOR “BENEFITED
PROPERTIES” AS THAT TERM IS DEFINED IN RULE 11, 23.5 AND RULE 23.6[s1]
Each application for a Water Use Permit shall
follow the process set forth in Rule 23.1.
A proper Applicant for a Water Use Permit may be the property owner or
any agent thereof. The application for a Water Use Permit shall be deemed complete when the
Applicant submits all of the following:
1. A completed Water Use Permit application,
2. A copy of the recorded Assignment Document, “An Assignment of a Portion of Monterey Peninsula Water Management District Ordinance No. 39 Water Entitlement and Water Use Permit” or “An Assignment of a Portion of City of Sand City Water Entitlement” specific to the application Site.
3. Processing
fees.
Section Five: Amendment of Rule 23.1, Action on Application
for a Water Use Permit on a Benefited Property
Rule 23.1[15]
shall be revised as shown in bold italics (bold italics) and
strikeout (strikeout):
A. PROCESS
1.
Action on Application for a Water Use Permit
a. The General Manager shall review the application and determine whether the Applicant has met the criteria for a Water Use Permit. If additional information is required to complete the application, the Applicant shall be notified in writing within thirty (30) days of the initial application.
b.
The General Manager shall ensure that the Assessor’s
Parcel Number of the Benefited Property shown on the Assignment Document
matches the APN(s) shown on the spreadsheet of water purchasers provided to the
District by either the Pebble Beach Company or the City of
(1)
When the APN(s) shown on the Assignment Document does
not match the spreadsheet of water purchasers, the General Manager shall notify
the Pebble Beach Company of the discrepancy contact the appropriate
Entitlement holder to verify the validity of the Assignment Document.
(2)
When the APN shown on the Assignment Document is determined
found
to be incorrect an error, the Applicant shall submit a
corrected and recorded Assignment Document from the Entitlement holder prior to
issuance of a Water Use Permit. The
Entitlement holder shall notify the District in writing of any correction.
(3)
When the APN shown on the Assignment Document is
determined to be correct and the spreadsheet is in error, the spreadsheet of
water purchasers shall be revised by the Pebble Beach Company to reflect the
correct APN.
c. The General Manager shall prepare and execute a Water Use Permit for the APN(s) shown on the Assignment Document.
d. The original Water Use Permit shall be mailed to the Applicant.
e. The District shall retain one copy of the Water Use Permit and the copy of the Assignment Document.
B. AMENDMENT
OF WATER USE PERMIT
1. A Water Use Permit may be amended to reflect a Change of Ownership of a Parcel.
2. A Water Use Permit may be amended to reflect assignment of water previously held collectively by two or more Parcels under a Water Use Permit. A written request for assignment shall be submitted to the District, along with processing fees and ownership information sufficient to prepare a new Water Use Permit.
3.
A Water Use Permit may be amended to reflect
newly-assigned Assessor’s Parcel Numbers when a Benefited Property is
subdivided into two or more Parcels. A
written request for amendment shall be submitted to the District, along with
processing fees, evidence of the subdivision approval by the land
use Monterey
Section
Six: Amendment of Rule 11, Definitions
[Definitions will be added to this section.]
Rule 11 definitions for Assignment Document,
Benefited Property, and Water Use Permit shall be amended in accordance with
Sections Four and Five above. A new definition
shall be added for Sand City Desalination Facility.
A. Unless the
context specifically indicates otherwise, the following words or phrases shall
be given the definitions set forth below and shall be permanently added to Rule
11, Definitions, of the rules and Regulations of the district. Revised text is shown in bold italics (bold italics). Numbering is provided for ease or review.
1.
Assignment Document – “Assignment Document” shall
refer to the document “An Assignment of a Portion of Monterey Peninsula Water
Management District Ordinance No. 39 Water Entitlement and Water Use Permit”
issued and recorded by the Pebble Beach Company or to the document “An
Assignment of a Portion of Monterey Peninsula Water Management District
Ordinance No. __
Water Entitlement and Water Use Permit” issued and recorded by the City of
2. Benefited Property – “Benefited
Property” shall mean those properties located in the unincorporated portion of
the Del Monte Forest described on Exhibit “A” to Monterey Peninsula Water
Management District Ordinance No. 109 or those properties located within the
jurisdictional limits of the City of Sand City pursuant to Monterey Peninsula
Water Management District Ordinance No. __.
3. Sand City Desalination Facility
– “Sand City Desalination Facility” means and consists of a municipally owned
300 acre-foot per annum reverse osmosis desalination plant which treats water
from the shallow, brackish Aromas Sands Formation, extraction and injection
wells, pumps, water mixing equipment, and additional pipeline to convey product
water to the California American Water pipelines.
Section
Seven: Publication
and Application
The provisions of this ordinance shall cause the
republication and amendment of the
permanent Rules and Regulations of the Monterey Peninsula Water Management
District.
Section titles and captions are provided for
convenience and shall not be construed to limit the application of the text.
Section
Eight: Effective
Date and Sunset
This ordinance shall take effect at 12:01 A.M. on
____________, 2008.
This ordinance shall not have a sunset date.
Section
Nine: Severability
If any subdivision, sentence,
clause, or phrase of this ordinance is, for any reason, held to be invalid or
unenforceable by a court of competent jurisdiction, such invalidity or
unenforceability shall not affect the validity or enforcement of the remaining portions
of this ordinance, or of any other provisions of the Monterey Peninsula Water
Management District Rules and Regulations.
It is the District’s express intent that each remaining portion would
have been adopted irrespective of the fact that one or more subdivisions,
paragraphs, sentences, clauses, or phrases be declared invalid or
unenforceable.
On motion of Director _________,
and second by Director ________, the foregoing ordinance is adopted upon this
_______ day of _____________, 2007, by the following vote:
AYES:
NAYS:
ABSENT:
I, David A. Berger, Secretary to
the Board of Directors of the Monterey Peninsula Water Management District,
hereby certify the foregoing is a full, true, and correct copy of an ordinance
duly adopted on the ______ day of ____________, 2007.
Witness my hand and seal of the
Board of Directors this ____ day of _________, 2007.
U:\GeneralEW)\MPWMD - Main\Gen 2007\Sand City Concept
Ord-3.doc
U:\General
(NEW)\MPWMD - Main\Gen 2007\Sand City Concept Ord-3.doc
U:\Arlene\word\2007\BoardMeetings\StaffNotes\111907\item14_exh_C.doc
[1] See Memo from District Counsel (Memo), Section I-A.
[2] See Memo, Section I-B
[3] See Memo, Section I-C.
[4] See Memo, Section I-D.
[5] See Memo, Section I-E.
[6] See Memo, Section I-F.
[7] See Memo, Section I-G.
[8] SWRCB
Letter dated January 31, 2006 from Celeste Cantu, Executive Director, to
[9] See Memo, Section II-A.
[10] See Memo, Section II-C.
[11] See Memo, Section III.
[12] See Memo, Section II-C and III.
[13] See Memo, Section I-D.
[14] For the current text of Rule 21-E, see Ordinance No. 128.
[15] For current text of Rule 23.1, see Ordinance No. 128.
[s1]Can’t we just refer to Rule 11?