EXHIBIT 21-E
MONTEREY PENINSULA WATER MANAGEMENT
DISTRICT
CONDITIONS OF APPROVAL
for
APPLICATION TO AMEND
WATER DISTRIBUTION
SYSTEM TO SERVE
APN 011-501-014, PERMIT #M10-07-L4
(Application #20080915MBS)
Permittee:
Permitted System:
Property Owner: Security National Guaranty, Inc.
Adopted by MPWMD Board on July ___, 2010 Pursuant to
Rule 22-D
Preparation Date: July _XX_, 2010
1. The California American Water (CAW) Water
Distribution System (Permitted System) is authorized by the Monterey Peninsula
Water Management District (MPWMD or District) under Permit #M10-07-L4 to serve the 39.04-acre parcel identified as Assessor’s Parcel
Number (APN) 011-501-014, the site of the proposed Monterey Bay Shores
Ecoresort (MBSE), based on use of water rights held by the Property Owner,
Security National Guaranty, Inc. (SNG).
Annexation of the subject parcel
was approved by MPWMD as part of Permit #M07-03-L4 (approved October 15, 2007),
but service is restricted pursuant to MPWMD Ordinance No. 132 (adopted January
24, 2008). The area to be
serviced is shown in Attachment 1. [Rule 22-D-1-a]
2. The Permittee is authorized by MPWMD under this Permit to provide potable water for commercial and residential use (mixed use resort) and associated landscaping to the parcel referenced in Condition #1, in compliance with approvals by the City of Sand City and California Coastal Commission. [Rule 22-D-1-b]
3.
The CAW
system capacity limit (“production limit”) for allowed extractions from the Coastal
Subareas of the Seaside Groundwater Basin shall be increased by up to 90 acre-feet per year (AFY) over the quantity specified in the Seaside
Basin Adjudication Judgment of March 27, 2006, Monterey County Superior Court
Case #M66343, as amended (“Adjudication Decision”), with the requirement that
this 90 AFY amount may only be used on the parcel referenced in Condition
#1, and water serving the parcel may only be derived from wells in the Coastal
Subareas of the Seaside Groundwater Basin. The expansion capacity (connection limit) is one master connection for the proposed
MBSE project, which may employ multiple water meters for effective tracking of
water consumption. The combined metered CAW water consumption on the
subject parcel shall not exceed 83.7 AFY, based on a system loss factor of
seven percent (7%). This factor, and
thus the metered sales limit, may be amended by the MPWMD General Manager if
documentation satisfactory to the District is provided by CAW to warrant such a
change. For the purpose of MPWMD’s Expanded
Water Conservation and Standby Rationing Program, up to 90 AFY reserved for the Property Owner will be added to CAW’s
recognized allotment, based on the Property Owner’s adjudicated water rights
specified in the Adjudication Decision referenced above, so long as CAW and the
Property Owner have a valid agreement for CAW’s use of water rights associated
with the subject parcel. [Rule
22-D-1]
4.
The
source of water for the Permitted System is groundwater in the Coastal Subareas
of Seaside Groundwater Basin. SNG’s rights
to this groundwater were adjudicated in March 2006. Water for the MBSE parcel shall be produced
by CAW and delivered to the MBSE parcel through CAW’s water distribution
system. All water provided to the MBSE
parcel must be derived from Wells in the Seaside Groundwater Basin, consistent
with the May 11, 2009 Monterey County Superior Court Order, Case #M66343
(“Court Order”) and the May 18, 2009 Agreement
Between Security National Guaranty, Inc. and California American Water
Regarding Front-Loading Delivery of Water (“Water Delivery Agreement”). [Rule 22-C-3]
Additional
Mandatory Conditions of Approval (Required by MPWMD Rules)
5. Precedent to use of this Permit,
Permittee shall also first obtain and comply with any required approval from
the local jurisdiction in which the property is located, in this case, the City
of Sand City. The California Coastal
Commission must also approve a MBSE coastal development permit. This Permit is not valid until the California
Public Utilities Commission recognizes CAW’s annexation of the subject parcel
identified in Condition #1 through the “Advice Letter” process. The Seaside Basin Watermaster confirmed on September 19, 2008 that CAW may
deliver water to the subject parcel using the Alternative Production Allocation
water rights held by the Property Owner.
The State Water Resources Control Board, Division of Water Rights,
confirmed on February 5, 2009 that the one-for-one replacement requirement in
Order WR 95-10 does not apply to the MBSE application so long as CAW water
supply for the project is derived from the
6. Permittee and Property Owner shall
execute an Indemnification Agreement, provided as Attachment 2, which holds the
District harmless and promises to defend the District from any claims, demands,
or expenses of any nature or kind arising from or in any way related to the
District approval of the Permitted System or the adequacy of the system water
supply. This Permit is not valid until
the Indemnification Agreement is signed by the Permittee, Property Owner and
MPWMD. The Indemnification Agreement
must be signed within 60 days of the preparation date shown (see top of page 1)
for this Permit to remain valid. [Rule
22-D-1-d]
7. Permittee shall comply with District
rules relating to water well registration, metering and annual reporting of
production (MPWMD Rules 52 and 54). It
is noted that two non-CAW wells also exist on the subject parcel, and the Property
Owner shall also comply with Rules 52 and 54 for these wells. [Rule 22-D-1-e; Rule 22-D-2]
8. The WDS system owners shall report
production by the Water Meter Method (MPWMD Rule 56) for the wells designated
in Conditions #4 and #7. [Rule 22-D-1-e;
Rule 22-D-2]
9. Permittee shall comply with all MPWMD
water conservation rules that pertain to CAW customers as applicable to the mixed-use
MBSE project (e.g., commercial, hotel, residential, landscape). Current ordinances specify maximum water use
rates for fixtures and require new development to install drought-resistant
landscapes, and drip irrigation, where appropriate. Contact with the District Permit and
Conservation Office at 831/658-5601 is recommended during project planning. [Rule 22-D-1-f]
10. No new Connections to the Permitted System may be set until a Water Permit has been secured from MPWMD for each connection in accordance with MPWMD regulations governing issuance of Water Permits. Connection charges shall be calculated based on water demand estimates using the District’s water demand methodology at the time of the application. [Rule 22-D-1-g]
11. Any intensification or expansion within
the Permitted System shall require a new application and Permit pursuant to
MPWMD Rules 23 and 24. [Rule 22-D-1-k]
12. Any new facilities, expansion of service
area boundaries, changed conditions regarding water service by other entities,
increase in the production or connection limits set in Condition #3, or other
changes described in MPWMD Rule 22-E shall require a Permit to amend the Permitted
System. [Rule 22-E]
13. No
permanent intertie between the Permitted System and any other system shall be
allowed in relation to the MBSE parcel. The
MBSE parcel may receive trucked-in water or water from the back-up well on the
property, as allowed by the Monterey County Health Department, in a non-fire
emergency, system failure or similar short-term critical event. Use of trucked-in water shall be guided by
MPWMD Rule 173. The subject parcel is
part of the CAW service area and may receive CAW water for emergency fire
service. [Rule 22-D-1-h]
14. A
back-flow protection device to prevent contamination of the CAW system is not required
as the subject parcel will be served by CAW. However, if use of non-CAW wells on the parcel
is contemplated, CAW and Property Owner must take appropriate action to ensure
that the CAW system would not be contaminated.
[Rule 22-D-1-h]
15. Because the Permitted System is a
regulated public utility that provides water to nearly 39,000 customers via an
extensive water system, compliance with California Title 22 drinking water
standards is already required by State Health authorities. [Rule 22-C-2]
16. Permittee is not required to carry out
specific mitigation measures by MPWMD above and beyond those already required
by the City of Sand City in its adopted Mitigation Monitoring Plan for the MBSE
project (approved December 1, 1998) as refined by the Addendum adopted by the
City on January 20, 2009. It is noted
that other agencies could refine or amend required mitigation measures.. [Rule 22-D-1-i]
17. Permittee is not required to provide a
copy of an agreement to serve water to the recipient parcel because it is
within the service area of a regulated public utility. It is noted that the Permittee has provided a
copy of an executed Water Delivery Agreement dated May 18, 2009 between CAW and
the Property Owner regarding use of 90 AFY of Alternative Production Allocation
water rights. [Rule 22-D-1-j]
18. Upon District approval of this Permit,
Permittee (and/or Property Owner) shall pay to the District the invoiced cost
for MPWMD staff, attorney and consultant time spent to process the Permit
subsequent to the application date, if required. The Permittee is not charged for the first 40
hours of staff time or equivalent. The Permittee will be provided documentation
to support the invoiced amount. This Permit is not valid until payment for the
invoiced amount is received by MPWMD. The
payment must be received within 60 days of the preparation date (see top of
page 1) for this Permit to remain valid.
[Rule 22-D-1-l]
19. Upon finalization of these conditions,
the Permittee and Property Owner shall sign and notarize a form regarding
acceptance of these Permit conditions for approval of the Permitted
System. By signing the form, Permittee
acknowledges that Permittee understands and accepts these conditions as a
binding part of the Permit approval, and agrees to carry them out faithfully. This Permit is not valid until the signed
acceptance form has been received by MPWMD. The Acceptance Form must be received within 60
days of the preparation date (see top of
page 1) for this Permit to remain valid.
[Rule 22-D-1-m]
20. Permittee and/or Property Owner shall
disclose to any future owner, successors and assigns of the property described
in Condition #1 (including owners of any future subdivided lot) the requirements
for the Permitted System associated with this Permit. MPWMD shall be advised in
a timely manner of any changes in system ownership, system name, or other
substantive changes to the system to facilitate accurate record-keeping. [Rule 22-D-2]
21. Construction tasks for water facilities
authorized by this Permit (e.g., service connection pipelines to the MBSE
parcel described in Condition #1) shall be initiated within one year from the latter
of (i) the date this Permit is issued, or (ii) the issuance of the Coastal
Development Permit, if applicable. This Permit
shall expire if no action is taken within that year. Water delivery to the MBSE parcel shall
commence within two years from the latter of (i) the date this Permit is
issued, or (ii) the issuance of the Coastal Development Permit, if
applicable. Permittee may apply in
writing to the MPWMD General Manager for a 180-day extension to either of these
deadlines, to be approved at the discretion of the General Manager. [Rule 22-D-4]
22.
Permittee
shall ensure that the Property Owner of parcel APN 011-501-014 shall execute a
Deed Restriction prepared by MPWMD regarding the limitation on water use as set
forth in these conditions. Permittee
shall pay all fees associated with preparation, review and recording of the
Deed Restriction. The Deed Restriction
must be signed and notarized by the Property Owner, and accepted by the
Monterey County Recorder for processing within 180 days of the issuance of the
Coastal Development Permit before a signed WDS Permit from MPWMD is transmitted
to the Permittee. [Rule 22-D-1-n]
23. ThePermit granted herein is subject to
revocation in the event Permittee and/or Property Owner do not fully comply
with each and every condition set forth in this Permit #M10-07-L4. [Rule
22-D-1-o]
Other
Conditions of Approval
24. Nothing in this Permit shall be construed
to grant or confirm any water right.
25. This Permit does not authorize any act
that results in the taking of a threatened or endangered species or any act
which is now prohibited, or becomes prohibited in the future, under either the
California Endangered Species Act (Fish and Game Code Sections 2050 to 2097) or
the federal Endangered Species Act (16 U.S.C.A. Sections 1531 to 1544). If a “take” will result from any act
authorized under this Permit, the Permittee shall obtain authorization for an
incidental take prior to construction or operation of the project. Permittee shall be responsible for meeting
all requirements of the applicable Endangered Species Act for the project
authorized under this Permit.
Special Conditions of Approval
26. District technical staff shall have reasonable physical access to the two existing dedicated monitor wells (#15S01E15F1 and F2) owned by MPWMD that exist on the subject parcel, and the Property Owner’s production well on the MBSE site (APN 011-501-014) for purposes of taking hydrologic measurements associated with water quality and quantity and/or to verify that they are properly maintained. Currently, data from the monitor wells are used by the MPWMD and the Seaside Basin Watermaster. Should modifications to the monitor wells to enable proper functioning and data collection be necessary due to MBSE construction and operation activities, these expenses shall be borne by the Property Owner.
27. The Property Owner and its successors shall provide copies to the District of any report required by the Watermaster, such as monthly water levels in its production well(s), the amount of water produced on a quarterly basis, and certain water quality test results on an annual basis each fall. Permittee shall annually provide to MPWMD a table of metered consumption records for all CAW meters serving the MBSE on the subject parcel for the period October 1 through September 30; this report shall be provided by November 30 of each year. The purpose of these data is to verify that the metered sales limit defined in Condition #3 is not exceeded. If deemed necessary by the MPWMD General Manager, the reporting period may be required to be more frequent (monthly or quarterly).
28.
Property Owner, and its successors, shall give notice
to MPWMD and provide copies to MPWMD of any required correspondence by the Watermaster
associated with transferring the type of right to produce water from the
29. CAW shall implement strict water accounting methods approved by the MPWMD General Manager to track CAW production sources to ensure: (a) only Seaside Basin wells (not Sand City desalination water) serve the MBSE parcel identified in Condition #1, and (b) no Carmel River Basin water is produced by CAW to serve the subject parcel, consistent with the May 11, 2009 Court Order and May 18, 2009 Water Delivery Agreement. CAW shall submit monthly reporting of daily MBSE-related water production data in the manner and form as prescribed by the District. The data tracking and reporting protocol shall be approved by the District General Manager prior to completion of construction of the MBSE project.
30. Consistent with the May 18, 2009 Water Delivery Agreement, CAW shall submit a written Operations Plan regarding the sole use of Seaside wells to serve the MBSE project to the District within 90 days of the preparation date shown (see top of page 1) for this Permit to remain valid. The Assessment shall include: (a) which Seaside wells are likely to be used to serve MBSE; (b) physical constraints associated with potential source wells and related infrastructure; (c) impacts to compliance with SWRCB Order 98-04, if any; (d) ramifications to the interagency Quarterly Water Supply Strategy and Budget process; and (e) estimated production from Seaside Basin well(s) in the winter “high flow” season to serve the MBSE parcel (and potential other customers, if required, due to well operation constraints). An extension of time to submit the report may be requested by CAW subject to approval by the MPWMD General Manager.
31. CAW shall provide to the District a copy of any quarterly report to the SWRCB, which may include information about service to the MBSE parcel identified in Condition #1.
32. The
Property Owner shall ensure that any use of its on-site wells on the MBSE
parcel identified in Condition #1 does not result in more than 149 AFY
extractions from the
ATTACHMENT 1 – Figure of service area for
Permitted System
ATTACHMENT 2 – Indemnification Agreement
U:\staff\word\boardpacket\2010\20100719\PublicHrgs\21\item21_exh21e.doc