EXHIBIT 8-D
MONTEREY PENINSULA WATER
MANAGEMENT DISTRICT
DRAFT
FINDINGS of
APPROVAL
CONSIDER
APPLICATION TO CREATE
SEPTEMBER RANCH WATER
DISTRIBUTION SYSTEM Service area: APN
015-171-010 and -012; 015-361-013 and -014
Application #20110316SEP, Permit #M12-06-L4
Adopted by MPWMD Board at November
____, 2012 Public Hearing
Unless noted otherwise, all cited documents and
materials are available for review at the MPWMD Office, 5 Harris Court,
Building G, Monterey (Ryan Ranch
It
is hereby found and determined as follows:
1. FINDING: September Ranch Partners, LLC, a California
Limited Liability Company, is identified as the owner of property located
at 676 Carmel Valley Road, Carmel Valley, which is the proposed location of an
approved residential subdivision (“September Ranch”) consisting of 73 new market-rate
residential lots, 22 new affordable housing lots, and one existing farm
house/caretaker unit; sales office/guard house; a 20.2-acre existing Equestrian
Facility with accessory structures; 536.4 acres of Common Open Space; 273.6
acres of Private Open Space and 6.9 acres of Open Space Reserved for future
public facilities. The subject parcels (APNs
015-171-010 and -012; 015-361-013 and -014) comprise approximately 891 acres. Following several years of environmental
review, the Monterey County Board of Supervisors approved the project on
November 9, 2010, based in part on a Monterey County Superior Court
determination of adequacy of the 2006 Final EIR, with the exception of water demand
estimates, which were further reviewed in 2009 and 2010.
EVIDENCE: MPWMD Permit Application #20110316SEP site map and application
materials dated March 16, 2011, including
all attachments; Grant Deed recorded by the Monterey County Recorder on December
30, 1987 (Reel 2183, page 788, ID#78206) and on October 27, 2011 (Document
ID#2011061569); Supplemental application information provided to MPWMD in
July-November 2012, including Summary of September Ranch Aquifer Depositional
Environment by Bierman HydroGeologic,
dated July 22, 2012. Monterey County
Board of Supervisors Resolution No. 10-312 dated November 9, 2010 (PC95062/PLN050001).
Draft and Final Environmental Impact
Report (EIR) for September Ranch Subdivision, SCH #1995083033 (2004); Draft and
Final Recirculated Portion of Revised EIR (February
and July 2006); Draft and Final Revised Water Demand Analysis (2009 and 2010); Kennedy/Jenks
Consultants, Final Report, Project Specific Hydrogeologic
Report, September Ranch Project, Carmel, CA 02/13/2006. Monterey County
Superior Court Peremptory Writ of Mandate (Case #M82632 and #M82643), issued December
23, 2008.
2. FINDING: The September Ranch Project is within the area served by
California American Water (Cal-Am), but Cal-Am does not currently have the
ability to serve the project due to current restrictions on its water
supply. Water will be provided by an
existing main Well (known as “SR-1”) and a minimum of one new Well. Existing
Wells A, B, and C will become monitoring Wells or recommended for destruction. Residential Cal-Am Meter #6258 and Commercial
Cal-Am meter #6276 will be disconnected.
EVIDENCE: Permit application materials as specified
in Finding #1; map of Cal-Am service area.
MPWMD Permit #M12-06-L4, Conditions of Approval #29 and 30.
3. FINDING: A Water Well Construction Permit for Well SR-1 was issued
by the Monterey County Health Department (MCHD) on September 5, 1990, and constructed
immediately thereafter. It was tested during
“dry season” conditions starting on September 6, 1990 to October 8, 1990. The
September Ranch Water Distribution System (SRWDS) will be installed pursuant to
the necessary water distribution system permits issued by the Monterey County Health
Department (MCHD). SRWDS will provide water for the project; however, each lot
of record must obtain an individual Water Permit from the Monterey Peninsula
Water Management District (MPWMD) allowing connection to the system. Each individual Connection will be metered.
The
SRWDS will be comprised of a primary Well (SR-1), back-up
Well(s), water treatment facilities, water storage
facilities, and water distribution and pumping facilities.
Water
will be drawn from the September Ranch Aquifer, as described in the technical
documents referenced in Finding #1. Total maximum pumping will not exceed 57.21
acre-feet per year (AFY). Each lot of record will maintain separate
water meters to ensure compliance with Monterey County and MPWMD Permit
parameters. Water will be treated prior to distribution utilizing a method that
consumes the lowest amount of water feasible within the range of 0 to 10% loss
rate. Water treatment alternatives will be reviewed and approved by the MCHD.
Storage
tanks and facilities will be constructed to provide maximum daily demand while
providing required flows and pressures. The proposed steel storage tanks will
be constructed in accordance with American Water Works Association (AWWA)
standards. Storage tanks and Well water will
provide fire protection for the project.
System
operation and maintenance will be performed under contract with Carmel Lahaina Utility Services Company or a comparable entity in
the business of operating and maintaining similar systems.
EVIDENCE: MCHD Water Well Construction
Permit #W5870; State Department of Water Resources
Well Completion Report #360102; Permit application
materials as specified in Finding #1; map of Cal-Am service area.
4. FINDING: Applicant has applied for a Permit to create the September
Ranch Water Distribution System (SRWDS) as described in Findings #1, #2 and #3.
The system will provide water only for the September Ranch Subdivision, with an
estimated water production of 57.21 AFY to provide potable and irrigation water
for domestic and landscape uses on the Parcels and uses as specified in Finding
#1.
EVIDENCE: Permit application materials as specified
in Finding #1, including water demand estimates.
5. FINDING: Based on District staff analysis of the engineering, hydrogeologic and environmental data provided in the
application, 57.21 AFY has been set as the annual production limit for the subject
WDS to meet the water needs for the Parcels and uses specified in Finding #1,
including conveyance and treatment losses.
EVIDENCE: Permit application materials as specified
in Finding #1, including technical and
environmental review documents;
Finding #17 of Monterey County Board of Supervisors Resolution No.
10-312, November 9, 2010. MPWMD Permit #M12-06-L4, Condition of
Approval #3.
6. FINDING: The application to create the September Ranch WDS, along with supporting materials, is in accordance with District Rules 21 and 22.
EVIDENCE: Permit application materials as specified
in Finding #1, including environmental, technical and water rights
documentation.
Required Findings (MPWMD Rule
22-B)
7. FINDING: The approval of the Permit would not cause unnecessary
duplication of water service with any existing system. The subject property is within the areas served
by Cal-Am, but Cal-Am water is unavailable for new or intensified use due to
existing limitations imposed by State Water Resources Control Board (SWRCB),
the Monterey County Superior Court, and the California Public Utilities
Commission (CPUC). The property also
appears to benefit from overlying water rights to percolating groundwater from
the September Ranch Aquifer as described in Finding #10. The proposed system will be limited to 99 Connections
for the uses described in Finding #1. [Rule
22-B-1]
EVIDENCE: Map of “Cal-Am” service area; MPWMD Permit
#M12-06-L2, Conditions of Approval #1 through #4.
SWRCB Order 95-10 dated July 1995; SWRCB Cease and Desist Order WRO 2009-0060
dated October 2009; Seaside Basin Adjudication Final Decision issued by
Superior Court dated March 2006; CPUC Decision 11-03-048 dated March 24, 2011. Water rights information submitted in
application materials specified in Finding #1 (Section 4.3 of 2006 Recirculated Portion of Revised Draft EIR).
8. FINDING: The approval of the Permit would not result in water
importation or exportation to or from the District, respectively. The referenced Parcels are located wholly
within the MPWMD. [Rule 22-B-2]
EVIDENCE: MPWMD boundary location maps.
9. FINDING: Approval of the application would not result in
significant adverse impacts to “Sensitive Environmental Receptors” (SER) as
defined by MPWMD Rule 11, including the Carmel Valley Alluvial Aquifer (CVAA). No active Wells owned by other entities are located
within 300 feet of the subject Well SR-1, and would not be adversely affected. [Rule 22-B-3 and Rule 22-C-5]
EVIDENCE: Permit Application materials as specified
in Finding #1, including all cited environmental, technical, legal and
regulatory documents. Sections
4.3.3 and 4.3.4 of 2006 Recirculated Portion of
Revised Draft EIR and Final EIR. Monterey County Board of Supervisors Notice
of Determination as a CEQA Lead Agency adopted November 9, 2010. MPWMD Notice
of Determination as a CEQA Responsible Agency dated November ____, 2012, following
public hearing held on November 19, 2012.
See also Finding #21.
10. FINDING: The
application adequately identifies the right of the September Ranch property
owner to the source of water supply for the subdivision, and provides
supporting verification in the 2006 Draft EIR. The proposed water source is the
September Ranch Aquifer, which is described as semi-isolated from the Carmel
Valley Alluvial Aquifer. The application and EIR identifies the claim of right to
include overlying use from percolating groundwater as well as a potential riparian
use. The EIR determines that the project
would not adversely affect other water rights holders in Carmel Valley,
including the CVAA, from exercising their rights. The Superior Court determined that the water
rights discussion in the 2006 RDEIR was legally sufficient. [Rule 22-B-4]
EVIDENCE: Permit application and environmental
documentation as specified in Finding #1, including Sections 4.3.1 and 4.3.2 of
the 2006 Recirculated Portion of Revised Draft EIR
and Final EIR. Monterey County Superior
Court Peremptory Writ of Mandate (Case #M82632 and #M82643), issued December
23, 2008. Grant Deed
showing ownership of property by applicant.
11. FINDING: The
application demonstrates existence of a long-term reliable source of water
supply for the proposed uses as described in Findings #1, and #4. The MPWMD staff concludes that the supply
should be adequate to provide water during peak and extended dry season periods
with the production limit of 57.21 AFY. The
MCHD has also determined that supply is adequate to meet the Parcel needs. [Rule
22-B-5]
EVIDENCE: Hydrogeologic assessments, engineering
analyses and Monterey County determinations in Permit Application materials provided in Finding #1, specifically Sections
4.3.3 and 4.3.4 of the 2006 Recirculated Portion of
Revised Draft EIR and Final EIR.
Monterey County Board of Supervisors Resolution No. 10-312 dated November 9,
2010 (PC95062/PLN050001).
12. FINDING: The
source of supply is identified as the separate September Ranch Aquifer, which
is described as semi-isolated from the CVAA.
The cumulative effects of issuance of a WDS Permit for the September
Ranch Subdivision would not be expected to result in significant adverse
impacts to the source of supply or the species and habitats dependent on the
source of supply. These impacts have
been evaluated by the County of Monterey as the CEQA Lead Agency and reviewed
by MPWMD as a Responsible Agency. [Rule
22-B-6]
EVIDENCE: Hydrogeologic
assessment and environmental review documents included in Permit Application
materials as specified in Finding #1 including Section 4.3 of 2006 Recirculated Portion of Revised Draft EIR and Final EIR.
Monterey County Board of Supervisors Resolution No. 10-312 dated
November 9, 2010 (PC95062/PLN050001). MPWMD
Permit #M12-06-L4, Condition of Approval #3.
13. FINDING: The
source of supply for the subject parcel is not derived from the Carmel Valley
Alluvial Aquifer or the Monterey Peninsula Water Resource System. The source of supply, the semi-isolated September
Ranch Aquifer (SRA), is unique in terms of the standard categories used by
MPWMD for well-based WDS. The SRA has
alluvial characteristics from a hydrogeologic
perspective but is treated as percolating groundwater from a water rights
perspective, as described in Finding #10.
The source of supply has been determined to be a less than significant tributary
to the source of supply for any other system. [Rule 22-B-7]
EVIDENCE: MPWMD map showing boundaries of project
site and jurisdiction of SWRCB superimposed on Monterey County parcels; technical and environmental review
documents submitted with Permit Application as specified in Finding #1. Water rights and hydrology reviewed in Section
4.3 of 2006 Recirculated Portion of Revised Draft EIR
and Final EIR.
14. FINDING: MPWMD
Permit #M12-06-L4 does not allow
a permanent intertie to any other water distribution system. The proposed WDS will be limited to a
physically and legally separate system and may not be connected to the Cal-Am
system at any time unless written permission from MPWMD is obtained. Temporary water service could be provided by
trucked-in water in a non-fire emergency such as system failure. However, emergency back-up supplies shall not
be drawn from the Carmel River, Carmel Valley Alluvial Aquifer, and/or the
Seaside Groundwater Basin. Fire-suppression
within the SRWDS service area will be provided by well water and on-site
storage tanks. In accordance with Monterey
County Condition of Approval #59 (Resolution No. 10-312), the fire protection
system will be permanently and immediately available. It is
noted that MPWMD Rules allow a separate standby Cal-Am meter solely for
emergency fire sprinklers in the ceiling of the applicable structures, pursuant
to local fire codes, because the Parcels are within the Cal-Am service area. [Rule
22-B-8]
EVIDENCE: MPWMD Permit #M12-06-L4, Condition of Approval #13. Monterey County Board of
Supervisors Resolution No. 10-312 dated November 9, 2010. MPWMD Rules and Regulations.
15. FINDING: A
back-flow protection device to prevent contamination of the Cal-Am system is
required, if deemed necessary by Cal-Am.
[Rule 22-B-9]
EVIDENCE: Map of Cal-Am service area; MPWMD Permit #M12-06-L4, Condition of Approval #14.
Minimum Standards for Granting a Permit (MPWMD Rule
22-C)
16. FINDING: The
application adequately identifies the Responsible Party as the owner specified
in Finding #1. [Rule 22-C-1]
EVIDENCE: Permit application and Grant Deed specified
in Finding #1.
17. FINDING: The
application meets the definition of a “Multiple-Parcel Connection System” and
will provide water for numerous uses; the water quality will comply with
California Title 22 water quality standards as administered by County and State
health authorities. [Rule 22-C-2]
EVIDENCE: Permit application materials specified in
Finding #1. MPWMD Permit #M12-06-L4, Conditions of Approval #1, #2, #3, and #15; California Administrative
Code, Title 22.
18. FINDING: The
application identifies the location of the source of supply for water
distribution system (water source and Well site). [Rule 22-C-3]
EVIDENCE: Permit application materials specified in
Finding #1, including location map. MPWMD
Permit #M12-06-L4, Condition of
Approval #4.
19. FINDING: The
approval of the application would not create an overdraft or increase an
existing overdraft of a groundwater basin.
As noted in Finding #14, in the event of system failure, emergency
back-up supplies will not be drawn from the Carmel River, Carmel Valley Alluvial
Aquifer, and/or the Seaside Groundwater Basin.
[Rule 22-C-4]
EVIDENCE: Hydrogeologic
assessment and environmental review documents included in Permit application materials
specified in Finding #1; MPWMD Permit #M12-06-L4,
Conditions of Approval #3 and
#13.
20. FINDING: The
approval of the application would not adversely affect the ability of existing
systems to provide water to users due to conditions of approval due to
conditions of approval by MPWMD and other entities that limit future water use
to a reasonable and acceptable amount, based on certified environmental review
documents. The property owner’s right to
use of September Ranch Aquifer water has been documented. [Rule 22-C-5]
EVIDENCE: Hydrogeologic
assessment and environmental review documents included in Permit Application
materials specified in Finding #1. Water rights and hydrology reviewed in
Section 4.3 of 2006 Recirculated Portion of Revised
Draft EIR and Final EIR. MPWMD Permit #M12-06-L4, Condition of
Approval #3. California
Water Code.
Compliance with California
Environmental Quality Act (CEQA)
21. FINDING: In
the review of this application, MPWMD has followed those guidelines adopted by
the State of California and published in the California Administrative Code,
Title 14, Section 15000 et seq. Specifically, the
MPWMD as a Responsible Agency under CEQA for this action has complied with
Guidelines Section 15096, and relies on actions by the County of Monterey, the CEQA
Lead Agency in this case. The MPWMD, as a Responsible Agency for this project, has
considered the County of Monterey’s Notice of Determination filed on November
10, 2009 approving the September Ranch Project based on EIR documents prepared
in 2004, 2006, 2009 and 2010 (listed in Finding #1 and below); Monterey County
Board of Supervisors Resolution No. 10-312 approving Permit PC95062/PLN050001
(as amended); Mitigation Monitoring Table approved November 9, 2010; Conditions
of Approval approved November 9, 2010. The MPWMD, as a Responsible Agency for
this project, has also considered the Peremptory Writ of Mandate (Case #M82632
and #M82643), issued December 23, 2008 by the Monterey County Superior Court.
MPWMD
Board members have been provided Compact Discs with copies of pertinent
environmental documents related to the September Ranch Subdivision
(SCH#1995083033), with emphasis on water issues, prior to the public hearing on
the SRWDS. The documents include: Draft
and Final EIR (2004), which was superseded by the 2006 version in relation to
hydrology and other water issues; Draft and Final Recirculated
Portions of EIR (February and July 2006); and Draft and Final Revised Water
Demand Analysis (2009 and 2010). The
MPWMD Board has reviewed the environmental information and relied on the
information as part of its decision-making on this matter.
EVIDENCE: CEQA and CEQA Guidelines, Section 15096. Permit Application materials as specified in
Finding #1, including all cited environmental, technical, legal and regulatory
documents.
22. FINDING: Pursuant
to CEQA Section 15091, the MPWMD Board finds that the project will not
have a significant effect on the environment, based on the documentation cited
in Finding #21. Mitigation measures are
not made as conditions of approval by MPWMD for this action. The full record
for the “September Ranch Subdivision Project” can be reviewed at the offices of
the County of Monterey, 168 West Alisal Street,
Salinas, CA. A CD with 2004, 2006, 2009
and 2010 environmental documents is available at the District office.
EVIDENCE: Findings and Evidence provided in Finding
#21 above. MPWMD Notice of Determination
for Approval of SRWDS as a Responsible Agency, issued
November ___, 2012
following public hearing on November 19, 2012.
23. FINDING: Pursuant
to CEQA Section 15093, a Statement of Overriding Considerations was not required
to be adopted by the MPWMD Board for approval of the subject Permit.
EVIDENCE: Findings and Evidence provided in Finding
#21 above. MPWMD Notice of Determination for Approval of SRWDS as a Responsible
Agency, issued November ___, 2012 following public hearing on November 19,
2012.
.
U:\staff\Boardpacket\2012\20121119\PublicHrng\08\item8_exh8d.docx