ITEM: |
CONSENT CALENDAR |
||||
|
|||||
6. |
CONSIDER expenditure for aquifer
storage and recovery well repair |
||||
|
|||||
Meeting Date: |
June 23, 2014 |
Budgeted: |
NA |
||
|
|||||
From: |
David J. Stoldt, |
Program/ |
Water Supply |
||
|
General Manager |
Line Item No.: |
1-2-1 A 1 |
||
|
|||||
Prepared By: |
Joe Oliver |
Cost Estimate: |
$112,430
(Reimbursable) |
||
|
|||||
General Counsel Review: NA |
|||||
Committee Recommendation: The Administrative Committee reviewed this
item on June 12, 2014 and recommended approval. |
|||||
CEQA Compliance: N/A |
|||||
SUMMARY: The ASR-1 well at the Monterey Peninsula Water
Management District (MPWMD or District) Phase 1 Santa Margarita Aquifer Storage
and Recovery (ASR) site is currently not operable due to an equipment failure
in late 2013 while the well was in service to supply water to the California
American Water (Cal-Am) delivery system.
The well pump’s line shaft and bearings will be replaced at a cost of
$107,077, plus 5% contingency. It is
intended that this work will be completed so the well will be available for
extraction operations later this summer and fall. The work is to be completed by the well
contractor that installed the recent upgraded equipment in the well, Zim
Industries, under change order contract.
RECOMMENDATION:
District staff recommends that the General Manager be authorized to prepare
a Change Order (contract amendment) with Zim Industries, Inc., the firm
currently under contract with the District, to complete the ASR-1 well equipment
repair work. This work will be completed
for the not to exceed amount of $112,430, which includes the base cost
($107,077) plus a 5% contingency ($5,359) in the event of unforeseen cost
variations. This work will commence as
soon as possible if this item is approved along with the Consent Calendar. Approval of this item will be contingent upon
final adoption of the FY 2014-2015 budget.
BACKGROUND:
The ASR-1 well was the first ASR well constructed in 2001 as part of the
District’s ASR feasibility testing program.
The original pumping equipment was test equipment that was not sized for
full-scale operations for the permanent ASR project. However, the original equipment continued to
be serviceable and was operated through the end of the Water Year (WY) 2012
season, when certain parts needed to be replaced. In 2013, the decision was made to upgrade to
the permanent pumping equipment, which was installed in August 2013. In December 2013, MPWMD staff was informed by
Cal-Am operators that the pump was experiencing irregular rotation stoppages
(or “seizures”) of the line shaft. In
late December, the equipment was removed from the well by Zim to further
investigate the problem.
The
new pumping equipment is a “water flush pump” design, which requires a
continuous source of pressurized water to lubricate the pump’s line shaft
bearings. Upon inspection of the
equipment, it was determined that at some point during operations, the source
of water to the shaft bearings was interrupted, causing excessive wear of the
shaft and bearings, which require replacement.
When the new equipment was being installed, an alarm system that could
detect a bearing lubrication interruption condition and force automatic shutdown
of the motor, was still in development. Due to the pressing need to get the well into
service for delivery operations (Cal-Am’s Paralta well had gone offline due to
a corrosion issue), it was agreed between MPWMD and Cal-Am staffs that the well
operation would require close observation of the water lube system functioning,
since the alarm system was not yet in place.
Subsequently, upon review of all available records that were kept during
the time the well was in operation before the problem was detected, it was not
possible to definitively determine the cause for the loss of shaft bearing
lubrication source water. Currently, the
alarm system is now designed and has been tested at the Phase 2 ASR wells
(Seaside Middle School site). It has
been ordered for the ASR-1 well, and will be placed in service when the
repaired equipment is installed. This
alarm system should prevent a similar line shaft water lubrication loss from
damaging the well equipment during future operations.
IMPACT
TO STAFF/RESOURCES: A significant staff effort has been expended
in planning, coordinating, analyzing and overseeing work on the District’s ASR
testing program in the Seaside Basin. This
current work is consistent with the District’s planning and budget for the ASR
project. As the repair work is related
to well operations and maintenance, it is reimbursable under the O&M
agreement with Cal-Am for the ASR facility.
Funding for this work is included under Line Item 1-2-1 A 1 of the FY
2014-2015 budget.