ITEM: |
CONSENT
CALENDAR |
||||
|
|||||
9. |
CONSIDER Expenditure of Funds to improve cooling
tower and rearing channel operations at the Sleepy Hollow Steelhead Rearing
Facility |
||||
|
|||||
Meeting
Date: |
April
19, 2021 |
Budgeted: |
Yes |
||
|
|||||
From: |
David J. Stoldt, General Manager |
Program/ |
Protect Environmental Quality |
||
|
|
Line Item
No.: |
2-3-1 A General
Operations Maintenance |
||
|
|||||
Prepared
By: |
Thomas
Christensen |
Cost
Estimate: |
$11,800 |
||
|
|||||
General
Counsel Review: N/A |
|||||
Committee
Recommendation: The Administrative
Committee reviewed this item on April 12, 2021 and recommended approval. |
|||||
CEQA Compliance: Categorical Exemption, Section 15301,
Existing Facilities. |
|||||
SUMMARY: Staff proposes to hire Telemetrix, a communications
consultant, to install a wet bulb temperature sensor to improve cooling tower
operations and a magnetic flow meter to monitor flow to the rearing channel. The equipment would be integrated into the Programmable
Logic Controller (PLC) that monitors and operates the Sleepy Hollow Steelhead
Rearing Facility. The cost of installation
and programming is estimated to be up to $11,800 (including a 15% contingency). Work should be carried out prior to the
initiation of 2021 operations at the facility.
RECOMMENDATION: The Administrative Committee recommends that
the Board approve the funds for installation and integration into the PLC.
DISCUSSION: After completion of a facility upgrade in the
spring of 2020, operations during summer and fall 2020 revealed two significant
issues: 1) the cooling tower can warm Carmel River flow used at the facility during
warm periods; and 2) debris and biofilm caused the flow meter for the rearing
channel to malfunction.
1) cooling tower and installation of a wet
bulb sensor
A large cooling tower was installed in
2000 with the capability to circulate about 800 gallons per minute (almost 2
cubic feet per second). This tower was
refurbished in 2020, but not as part of the overall facility upgrade (the tower
requires periodic maintenance). The
tower works as an evaporative cooler, i.e., air is drawn into the tower through
media filled with river water, a part of which “evaporates” and cools the
surrounding water passing through the media.
The cooler generally cools outside air by 15-25 degrees; however,
afternoon temperatures at Sleepy Hollow are often in the mid-to high 90’s (°F)
and there are short stretches of temperatures over 100 °F, sometimes with high
levels of humidity (which reduces the effectiveness of the cooling tower).
Through monitoring of temperature sensors
at the cooling tower inlet and outlet installed with the facility upgrade in
2020, it was determined that running the cooling tower fan on warm afternoons
resulted in heating the river water flowing to the rearing channel through the
cooling tower, rather than cooling the water.
Manually turning the cooling tower fan on and off (either when on site
or remotely) proved to be inefficient, as there are diurnal changes in air
temperatures and humidity at the site and the time of day when these changes
occur constantly.
Staff asked Telemetrix (TMX) to propose a
method to automate operation of the cooling tower fan. A two-phased approach is proposed: 1) install
a wet bulb temperature sensor, which measures the lowest temperature that can
be achieved purely by evaporative cooling; 2) tie the sensor into the PLC and
reprogram the PLC to operate the cooling tower fan based on wet bulb
temperature (this is a standard industry practice for cooling tower
operations).
Installation of the wet bulb sensor and linking
it to the PLC would allow the PLC to automatically turn on the cooling tower
fan when temperature and humidity conditions allow cooling of the water and
turn it off when running the fan would heat water.
2) rearing channel magnetic meter
Flow to the rearing channel is currently
monitored using a “paddle wheel” style meter that has a small paddle wheel
inserted into the delivery pipe to the head of the rearing channel. The paddle wheel clogged in 2020 due to
debris and biofilm and had to be removed, cleaned, and reinserted (at a cost of
$500). Accurate flow measurement at the
head of the rearing channel is needed to determine that flow is going to the
channel and is a factor used in determining steelhead density and habitat
quality. A magnetic meter does not have
clogging issues because a magnetic field is used to measure flow in the pipe
and there is no part of the instrument in the pipe flow.
TMX was the controls subcontractor for the
facility upgrade, has extensive experience with the onsite equipment, and
installed and programmed the PLC for the facility.
IMPACTS ON STAFF AND RESOURCES: Funds for this work were included in the mid-year
FY 2020-2021 budget adjustment under Program line item 2-3-1 A. General
Operations and Maintenance.
EXHIBIT
9-A March 20, 2021 Cost Estimate from Telemetrix